A few weeks ago I started a thread VFD on 1PH . I got back there today for another project and thought I would check the input current on the VFD. Line current of the single phase input is 2 amps for 1 of the output. When the pump motor is at full speed, fully loaded @ 60Hz the amp draw was about 25.5 according to the VFD display. Input was 51. Fluke 337 true RMS.
The recommended VFD for this single to three phase conversion was rated 30 hp @ 230 v. Input amps of 98 put my supply @ 125 amp single phase.
Nothing like having a little to spare.