Hi,
I have a question about the infeed protection of the drives. Manufacturer specifies the max amp rating for branch circuit protection. In our case, we usually use oversized drives to fulfil peak load requirements, however, motor is quite small in size. In this situation, we usually set the drive's infeed protection per motor FLA, multiplying it by 125%. For example, a 17.9A@460V motor being fed by 25 Amp drive (Manufacturer's recommendation for max. branch circuit protection is 80A). We have set drive infeed protection device (MSP) to 22.4A. Is it ok, or it should be set according to VFD infeed current and not the motor? Thank you!
I have a question about the infeed protection of the drives. Manufacturer specifies the max amp rating for branch circuit protection. In our case, we usually use oversized drives to fulfil peak load requirements, however, motor is quite small in size. In this situation, we usually set the drive's infeed protection per motor FLA, multiplying it by 125%. For example, a 17.9A@460V motor being fed by 25 Amp drive (Manufacturer's recommendation for max. branch circuit protection is 80A). We have set drive infeed protection device (MSP) to 22.4A. Is it ok, or it should be set according to VFD infeed current and not the motor? Thank you!