Overload of a 225A 125 VDC panel?

Status
Not open for further replies.

Bugman1400

Senior Member
Location
Charlotte, NC
I am looking at a load schedule for a 125 VDC panel that seems to be rated at 225A. The existing load seems to show a total of 28,000 watts. I am reviewing a proposed load total of 28,800 (800 additional watts). Overloaded?
 

Besoeker

Senior Member
Location
UK
I am looking at a load schedule for a 125 VDC panel that seems to be rated at 225A. The existing load seems to show a total of 28,000 watts. I am reviewing a proposed load total of 28,800 (800 additional watts). Overloaded?
Unless code requires a certain margin, you are at the limit, not over it.
 

Ingenieur

Senior Member
Location
Earth
125 x 225 = 28125

if the 28000 is actual continuous load you are pushing it
800 more would technically be ol'ed imo

125 DC?
substation battery power?
 