My question is about using one motor overload to protect multiple fractional hp fan motors.
Can I use one adjustable overload device to protect 3 fan motors? They are ½ horsepower motors, 480 volt, 3 phase. My thought was to check the running amps of all three and set the overload just above my reading. The full load of each motor is 1.1 amps. Operating they each draw .8 amps. If I set the overload to 2.5 it would trip if any one motor went over the 1.1 rating.
Can I use one adjustable overload device to protect 3 fan motors? They are ½ horsepower motors, 480 volt, 3 phase. My thought was to check the running amps of all three and set the overload just above my reading. The full load of each motor is 1.1 amps. Operating they each draw .8 amps. If I set the overload to 2.5 it would trip if any one motor went over the 1.1 rating.