Overload setting 430.6 A (1) question
thewire
Raleigh
So I am given this 3 phase AC squirrel cage motor with nameplate data as
power: 25 hp
service factor: 1
temperture rise: 60C
full load rating: 68A
voltage 230V
Locked rotor: D
Which overload setting should I used?
I thought based on the 430.6 A (1) exception 3 stated if both hp and full load rating are given, we should use the nameplate rating instead right?
power: 25 hp
service factor: 1
voltage 230V
Locked rotor: D
430.6(A)(1) ex 3 deals with "listed motor-operated appliances," not motors in general.
I think 430.6(A)(2) tells you what you are looking for with regards to overload protection.
(In this case, it looks like the table full load current and the nameplate full load current are the same.)
power: 25 hp
service factor: 1
voltage 230V
Locked rotor: D
I would look at 430.32
ah...that is confusing...listed motor operated appliances..