Yes, some are simple other ways will take the use of a meter. Is their a motor on the circuit? What's the circuit powering?There is some way to know in first instance if the breaker tripping was due overload, shortcircuit or ground fault conditions?
You will need to repeat the circumstances or rely on witnesses unless it’s the latest greatest AFCI/GFCI dual function. They will have trip codes stored in them.There is some way to know in first instance if the breaker tripping was due overload, shortcircuit or ground fault conditions?
Likely overloading. Takes time to warm up thermal trip function when cold starting. If restarting soon after trip, it is still warmed up from previous run and will trip in less time. Let it cool completely down and you get the longer time again on first try.Thanks all for your replies, I've pump in the circuit with nameplate 10Hp, 3f, 208v, the OCPD on and take few minutes to trip, and after switch on again, the trip is almost immediately.
Some suggestions is very appreciate.
Thanks
That won't fix the overloading if that is what is happening. Measure motor amps to confirm overloading. If overloaded you still need to determine why. With a centrifugal type pump might just be that it needs some restriction in the line to limit flow.Thanks, I'll do that