Overload, Shortcircuit or Ground fault?
marcosgue
Tampa
There is some way to know in first instance if the breaker tripping was due overload, shortcircuit or ground fault conditions?
Short circuits usually cause protective devices to operate in less than 1 sec, while overloads can take several seconds to minutes.
Ground fault timing depends on the protective device, but it is possible for a GFCI to take a few secs although they are usually immediate.
Might be better to classify as thermal overload, magnetic trip or ground fault type trips?
Thermal overload being somewhat of a low level but yet over the device rating that can take anywhere from many seconds to even a hour or two to trip, magnetic trip being high level fault current from either line to line or line to ground faults or ground fault being low level current that requires GFCI/GFPE sensing technology to detect.
Thanks all for your replies, I've pump in the circuit with nameplate 10Hp, 3f, 208v, the OCPD on and take few minutes to trip, and after switch on again, the trip is almost immediately.
Some suggestions is very appreciate.
Thanks
Thanks
Likely overloading. Takes time to warm up thermal trip function when cold starting. If restarting soon after trip, it is still warmed up from previous run and will trip in less time. Let it cool completely down and you get the longer time again on first try.
Thanks, I'll do that
That won't fix the overloading if that is what is happening. Measure motor amps to confirm overloading. If overloaded you still need to determine why. With a centrifugal type pump might just be that it needs some restriction in the line to limit flow.
Positive displacement type pump may be just the opposite issue, too much resistance to flow is going to load those harder.