Hello, working on an issue with a AB 193-1EFDB overload installed on a recirculating glycol system. There are four of these overloads in place and so far two of them have been "commissioned" but continue to trip. Amp draw on the pumps is almost exactly what is stated on the nameplate but we can't get more than 5 seconds of run time before the OL opens up. We're working with 208v single phase pumps, one of the pumps is .75hp and the other is 1hp. Current thought is that this overload shouldn't be used with pumps but I can't find a reason why they would be failing. If we bypass the overload the pumps run with no issue and normal amp draw. Initial load is about 20amps but drops off right away down to 6-7 amps on each motor. Currently the OLs are set to 15 amps with the trip class set to 30.
Thank you