tjacobs
Member
- Location
- Moorestown, NJ
when wiring a stop start motor control circuit do the overload contacts belong on the hot or the neutral side of the coil ?
Please explain why.
TIA
Please explain why.
TIA
Think about decades of traditional industry practices in North America and Europe. Has one method proven to be more problematic than the other?General rules are that all switching be done in the ungrounded conductor(s) yet is very common to see overload contacts in the grounded conductor in control circuits. I don't know why. Overload contact is very commonly placed in the "L2" side of the circuit whether it is a grounded conductor or not though and all the normal controls are all in the "L1" side of the circuit.
I was told by an old timer a long time ago that it had something to do with a situation where there was a loss of power while running.General rules are that all switching be done in the ungrounded conductor(s) yet is very common to see overload contacts in the grounded conductor in control circuits. I don't know why. Overload contact is very commonly placed in the "L2" side of the circuit whether it is a grounded conductor or not though and all the normal controls are all in the "L1" side of the circuit.
You are referring to a 3 wire start/stop which will not restart automatically after a power interruption. This is unrelated to the OP question.I was told by an old timer a long time ago that it had something to do with a situation where there was a loss of power while running.
When power is restored you could have the motor automatically start. Can't remember what the scenario was.
.
I don't see it being a problem functionality wise, just seems odd that in general we not supposed to switch grounded conductor yet we do so with these motor overload contacts quite often.Think about decades of traditional industry practices in North America and Europe. Has one method proven to be more problematic than the other?
A ground fault won't energize the coil, it can bypass the overload protection though.As discussed, in the NEMA world the factory OLs are in the grounded conductor when 120 coil is used. But this side of the circuit can't be extended beyond the controller enclosure due to the possibility of a ground fault energizing the coil. This has been in the NEC for decades. See 430.74.
It could depending on the control circuit setup.A ground fault won't energize the coil, it can bypass the overload protection though.
If standard three wire control with holding contact, it shouldn't.It could depending on the control circuit setup.
Who said I was speaking of only 3 wire control. Why do you always state the obvious?If standard three wire control with holding contact, it shouldn't.
If start switch or holding contact stuck closed for any reason contactor is pulling in anyway unless overload contact opens. Then any bypass to ground will still allow to pull in but you also have overload bypass situation which is bad even if no other problems with start/holding contact.
Because there are many that read these threads, don't post and do not have the experience or education of others here.Who said I was speaking of only 3 wire control. Why do you always state the obvious?
I thought we were talking about a three wire control, maybe we weren't?Who said I was speaking of only 3 wire control. Why do you always state the obvious?
when wiring a stop start motor control circuit do the overload contacts belong on the hot or the neutral side of the coil ?
Please explain why.
If the starter coil is 120 Volts AC then the overload block is wired to the grounded conductor ( yep neutral ). I for one questioned this to my shop teacher over 50 years ago for not being the safest way. If for some reason the other end of the overload block was to be grounded you would loose critical motor overload . More then once I have seen somebody disconnected the neutral side of motor starter and run it out to limit switches.
Me too. The OPs post infers 3 wire control by stating “start stop control circuit”, which I interpreted as being a start button and a stop button, the definition of a 3 wire control circuit.I thought we were talking about a three wire control, maybe we weren't?
I believe that only having halve of the coil voltage would not produce any where near the magnetism required to pull in a starter. Years ago think it was Cadillac best of the best Allen Bradley had it in their thick product catalogue the minimum required voltage percentage to what they call to seal the starter contacts. Had to be over 85%. Have to be carefull when selecting the minimum size controll transformer when installing several motor starters especially if they are all capable of starting at the same time. Some people only used the sealed current ( maybe 13 to 18 watts for a NEMA size 1 starter ) and not the current it takes to seal contacts. Some Danfoss FC model early drives with the 3 starter bypass function had problems because of slightly undersized control transformer. They placed a 5 to 10 second time on delay timer so only the M1 start contactor that feed the drive would energize then 5 to 10 seconds later the M2 drive output contactor would pull in. Learned so much from drive tech that performed start ups. Would always have a question or two for them and learned more about drives then a few drive classes I attended.If you had a 240 volt coil and still had the overload contact in the L2 side but all other controls in the L1 side, which is pretty common, you could still have unexpected coil pull in if there is a ground fault between coil and the overload contact (and overload is open). The coil would only be seeing 120 volts, and is subject to overheating because of the low volts but if enough to cause pull in still can start the controlled load. Larger the contactor the less likely it can pull it in as well though.