overloading of ordinary dry type transformers
mshields
Boston, MA
Do dry ordinary dry type transformers have overload characteristics. In particular, I've got a 45kVA, 150deg rise 480 to 208Y/120V that we'd like to overload for a limited period of time on a temporary basis if possible. I realize, I'd be in good shape if it were a 115deg or 80deg rise, but it's not. Do you know if the vendors have published data on this?
Note: All my vendor contacts are out. Thought I might have some luck here.
Thanks,
Mike
Overloading within limits
Dry-type transformers are available in standard temperature rises of 80°C, 115°C, or 150°C. These values are based on a maximum ambient temperature of 40°C for spot temperatures and 30°C average ambient temperature over a 24 hour period. That means, for example, that an 80°C rise dry transformer will operate at an average winding temperature of 120°C when at full-rated load, in a 40°C ambient environment without damaging any one spot on the transformer winding, however, if a long time period of loading is expected the 30°C ambient average is a better target to use since hot spots within the transformer may be at a higher temperature than average. Most dry transformers use the same insulation on their windings (typically rated at 220°C), irrespective of the design temperature rise, the 80°C rise unit has more room for an occasional overload than a 150°C rise unit, without damaging the insulation or affecting transformer life. However, the 150°C unit is better able to cool itself from a temporary overload than an 80°C unit. Thus the 150°C rating even though it will be less efficient than the 80°C unit. Overall the insulation rating is given as the temperature rise + maximum ambient + Hot Spot Allowance = Maximum wind temperature. Thus 150° + 40° + 30° = 220°C.
You do have to be careful when determining temperature rise also sine the ANSI definition of temperature rise is the average rise as determined by change in D.C.resistance of the windings. You may have about a 15% margin to play with but an alternative may be to add forced cooling in the form of fans to draw air through the unit at a higher than normal CFM cooling flow with natural convection. I would suggest you check with the manufacturer for recommendations.
Hope this helps,
NewtonLaw
Thanks,
Mike
Interesting that you omitted to state what the overload would be and how long you expect it to last in addition to what the average ambient temperature would be which are all important factors that must be considered.
Based upon your transformer short term overload is designed into transformers as required by ANSI. Basically DTDT is capable of delivering 200% nameplate load for 1/2 hour, 150% load for 1 hour, 125% load for 4 hours provided that a 50% load preceding and following the overload. Ref. ANSI C57.96-01.250 FG or additional limitations.
In my opinion, IEEE Std C57.96/2013 it could be useful.
In my old edition, IEEE Std C57.96-1999 :ashamed1: IEEE Guide for Loading Dry-Type Distribution and Power Transformers ch. 6. Basis for calculations of temperatures, loss of life, and loads
it is a way how to calculate the allowable overload.
You may consider at first the equivalent load[equation 3]:
Leq=[(L1^2*t1+L2^2*t2+...Ln^2*t3)/(t1+t2+...tn)]^0.5
where L1..Ln are the load steps in % of rated t1...tn duration of these loads.
The calculation will take into consideration the life shortening of the winding insulation. The maximum life is considered to be 20000 hours and each overload will shorten this in a way.
In ch.3. Basic loading conditions for normal life expectancy there are 3 tables[4.5 and 6] and for
example
Table 4 for 150oC rated insulation 20oC ambient the overload could be 56% for 1/2 hr. if the load before or following is not more than 90% for 50% load the permissible overload could be 71%.
However, if the ambient temperature will be 40oC then the instead of 56% will be only 33% and instead of 71% only 59%[Table 6]