240.21(B)(3) is the 25' tap rule for transformers, which lets the conductors landed on the primary transformer terminals be taps. To paraphrase the 5 requirements listed, they are:
(1) The primary tap conductors must be at least 1/3 the ampacity of the OCPD protecting them from SCGF.
(2) Likewise for the secondary conductors, after you adjust for the transformer current ratio.
(3) One primary conductor plus one secondary conductor must add up to 25' or less.
(4) The primary and secondary conductors must be protected from physical damage.
(5) The secondary conductors terminate in a single OCPD that provides overload protection for them.
Missing from this formulation is any requirement that the secondary OCPD provide overload protection for the primary tap conductors, which seems like a clear oversight.
In other words, what section would the following install violate:
-25 kVA 240V : 240V 2-wire : 2-wire isolation transformer supplying 12 kVA of load
-Primary OCPD is 125A
-Primary conductors are 10' long, 50A ampacity
-Secondary conductors are 10' long, 100A ampacity
-Secondary OCPD is 100A
Cheers, Wayne
(1) The primary tap conductors must be at least 1/3 the ampacity of the OCPD protecting them from SCGF.
(2) Likewise for the secondary conductors, after you adjust for the transformer current ratio.
(3) One primary conductor plus one secondary conductor must add up to 25' or less.
(4) The primary and secondary conductors must be protected from physical damage.
(5) The secondary conductors terminate in a single OCPD that provides overload protection for them.
Missing from this formulation is any requirement that the secondary OCPD provide overload protection for the primary tap conductors, which seems like a clear oversight.
In other words, what section would the following install violate:
-25 kVA 240V : 240V 2-wire : 2-wire isolation transformer supplying 12 kVA of load
-Primary OCPD is 125A
-Primary conductors are 10' long, 50A ampacity
-Secondary conductors are 10' long, 100A ampacity
-Secondary OCPD is 100A
Cheers, Wayne