I personally believe that a contractor had a bad transfer switch that he unloaded on one of my customers. He put in a Siemens 3200A transfer switch on a 1200A application. Currently the application is not code, he put in a 2000A trip plug but there is no lock on the door so I don't believe that adjusting an adjustable trip meets NEC 240. However, the switch has not worked properly during testing, the CT's look old and in general I don't like the installation. The transfer switch is breaker based and I prefer double throw. In general I don't like having a bigger breaker than what is called for and I don't see why anyone would do it for a good reason.
Please comment. Help me to get this bad installation completely ripped out instead of having the contractor come back and mess with it and mess with it like he has for six weeks or more. The building is dark.
As many of you know I am a design engineer. Feel free to disagree with me - I would love to be prepared for whatever arguments I may receive. Thanks.