iwire said:Not a violation although it may be hard to terminate it on cheap devices.
celtic said:...and nobody has a recpt. just laying about they could just pick up and read????
iwire said:Doh! good point.
iwire said:Doh! good point.
The ones within my reach are Leviton CR20 (formally 5800)
It is listed for 10 AWG but they are spec grade 20 amp duplexs
I would really like to see one from the $0.45 bin at HD.
tbonse said:As for the $0.45 duplexes, I'd rather just see them remain in that bin and get the 20A ones from a couple shelves up.
If I remember correctly, the little cheapies are rated for 14awg and 12awg. I don't have one sitting around to check, and it's kindof late for a Home Depot run.
infinity said:Sure the 20 amp spec grade duplex receptacles may be better, but now you'll need 20 amp circuits.
iwire said:Not a violation although it may be hard to terminate it on cheap devices.
Read a little further to Table 210.21(B)(3) and see that recps on 15A ckts can be "Not over 15" amps.celtic said:15A ckts are fine...see 210.21(B)(2)
Read a few posts back...jeff43222 said:Read a little further to Table 210.21(B)(3) and see that recps on 15A ckts can be "Not over 15" amps.
infinity said:Sure the 20 amp spec grade duplex receptacles may be better, but now you'll need 20 amp circuits.
celtic said:15A ckts are fine...see 210.21(B)(2)
which goes back to 210.21(B)(1)..which is also agreed upon in T210.21(B)(3)A single receptacle installed on an individual branch circuit must have an ampere rating not less than that of the branch circuit. For example, a single receptacle on a 20-ampere individual branch circuit must be rated at 20 amperes; however, two or more 15-ampere receptacles or duplex receptacles are permitted on a 20-ampere general-purpose branch circuit. This requirement does not apply to specific types of cord-and-plug-connected arc welders.
kingpb said:Why not just pigtail with #12AWG?
celtic said:Read a few posts back...
You can put 2 or more 20A devices on a 15A ckt...
...which was the point of:
infinity said:You're not reading the table correctly. Look at table 210.21(B)(3)
Circuit rating of 15 amps, receptacle rating not over 15 amps.
celtic said:Isn't that what I meant to say?