I have access to a 60 kva isolation transformer for 480v to 380v. My customer only has 30A at 480v. Can we use this transformer for loads that don't exceed the 30A at 480 / approx 38A at 380v?
Is there a way I can reduce inrush current? Maybe wire a small 3ph 380v motor (with proper OL and OC protection)to the secondary to be energized only at startup? I have heard that a loaded secondary actually causes a lower inrush.
Doug -
I didn't see any reference in your OP to the feeder being fuses, so I'll assume the feeder is a 30A molded case, thermal magnetic circuit breaker.
Is this a permanent install, or temporary?
If temporary - go for it. If it trips, try 4, 5, 6, 10 times. If/when it holds, do your work.
If permanent, I would say, No.
Inrush on a 60 kva xfm ~ FLA x 10 = 720A, well into the instantaneous range of a 30A CB.
GE says the max inrush will occur 1 time in six energizations.
I have seen transformers ooze on-line, but not often.
As for a secondary load reducing the inrush, I have also heard that. I have never seen any ieee papers or any other test data supporting this. Gar's example is interesting, however I don't know how extensive the test data is.
As for a transformer with a small feeder, oozing on-line, I have seen a
few examples. all were temporary power and In each case, I fully expected a trip. They didn't and I didn't try a second time.
And, no, 30A time delay fuses are not significantly better at transformer energization.
About the best you can do with a 30A, 480V, circuit, will be about 20KVA. Nope never seen a 20KVA, 3ph xfm. Then again, I have never heard of a 60KVA, 3 ph xfm. Normal sizes are:
15 kva
25
37.5
50
75
100 kva
If the goal is to reliably energize a 60kva transformer, normal inrush characteristics:
Feed with an FLA x 1.25 CB >> 72 x 1.24 = 90.2A, use a 100A CB, #2 CU.
Good luck. Let us know haw it goes