I have a client that has oversized generators for their systems. For example, they have a 400-amp 200kw generator feeding a 200-amp ATS and 200-amp service. When brought up to the engineering team they said to upgrade the lugs on the ATS to accommodate the 350 kcmil from the generator. However, I feel that this is still violating a few different NEC codes ie. 700.4, 110.3, and 240.4. I am hoping to get the soundest code violation that I can bring to them. Let me know if I am wrong.
I also feel like this is going to cause extra maintenance like load banking.
Let me know what you all think and thanks in advance.
I also feel like this is going to cause extra maintenance like load banking.