Well I am a telecom power engineer and can shed some light on the subject, however I doubt it will satisfy you.
Number one reason is to keep the voltage drop between N-G below 2 VAC P-P. The reason is the way switch mode power supplies operate.
Number two reason, to a lessor degree is neutral over heating. Harmonics cannot be controlled by the size of the neutral. We use delta/wye transformers to control harmonics and isolate them.
I have worked for three telecom's, SBC, MCI, and currently Alltel over the last 25 years and all three have similar practices which go something like this.
All prefer 480/277 service using a 480 delta UPS system to supply critical 120 VAC loads via a device called a PDU. The PDU uses a K-13 step down transformer with built-in filtering, monitor, alarms, and distribution. The PDU allows a new ground reference point to be established via N-G bond. General purpose recepts use a K-4 or standard transformer. The main difference between all of them is the size of the neutral they use, and for what type of loads. Could be 100, 141 or 200%. I use 100% neutral feeder for general purpose loads, 141% neutral feeder for critical equipment loads, and never 200%.
The rest of the equipment like HVAC, mechanical, rectifiers, etc are all 480 delta, and lighting is 277.
Keep in mind telephone companies primarily use -48 VDC operated equipment. Harmonics are not a problem there. It is the data equipment like servers, routers, hubs ect that use AC power, and the evolution of what we call collo hotels that complicate things. Collo hotels are areas set up to lease space to companies like AOL, Earthlink and the like to give them direct access to the network we provide. BIG BUCKS. The problem is every Tom, Dick, and Harry do things differently if they even have a clue what they are doing, and we have to provide an environment that accommodates all their needs. If not someone else will.