I have a job that the customer want to use a spare 25 HP VFD to run a 7-1/2 HP fan motor.
I know that according to 430.122 I need to size the feeder to this VFD at 125% of the VFD input current.
Do I size the load side conductors of the VFD at 125% of the motor full-load current as per 430.22 or the same as the input current conductor size?
I know that according to 430.122 I need to size the feeder to this VFD at 125% of the VFD input current.
Do I size the load side conductors of the VFD at 125% of the motor full-load current as per 430.22 or the same as the input current conductor size?