oversized wire for 20A circuits
Hello I have a project where the Engineer requested that we pull #4 copper for (4) 20A circuits due to the footages. The issue is that #4 will not terminate onto a Siemans 20A breaker. The max for the breaker is #10. Can you use a pin adapter? Has anyone doe this?
By my calculations, you need to be looking at 400 foot runs, to warrant using #4. Is that what you are dealing with?
You can use few inches of #10 at the breaker, transition up to #4 for the run, then transition back down to #10 (or even #12) when you get close to the load. I don't know what devices are available to do this job, but the NEC will allow it.
Please note that the EGC will have to be #4 for this run.
If this is for lighting on a contactor, just run #10 between the breaker and the contactor. You may or may not have the same issue at the contactor, but most are rated for 30a, so they'll take larger conductors than a breaker.
These circuits are are for critical sever's for computers. The run is 550' long. I guess we can add a can above the panel and use some insulated termial blocks to downsize the wire. I was trying to avoid that due the lack of space in the ceiling. Someone mentioned compression pin adapters.
ilsco is one of the manufactures that make reducing pin(s).
>> It comes up as an unsecure web page << but
Here is a direct link to their ACM AL Pin (compression)
Would running a subfeed and setting a small panel near the equipment be to your advantage? Are these 120 or 240V circuits?
Why?
There is nothing in the NEC that dosent allow splicing in a panel?
As an IT person, if my sole source of critical power is coming from 550 feet away I'd be quite worried, lots of bad things can happen on a run that long. Of course, it may be that this is not the sole source or there is close by resiliance, such as UPSs.