Hello all,

Running into situations where I need to run #6 conductors on 30A branch circuits feeding L6-30Rs for some network switches. Of course the 30A breaker and the L6-30R only accept up to #8 conductors on the terminals. Anyone aware of a product ( a ferrule perhaps?) that would make it possible to terminate the #6 conductors on the breaker and receptacle? The client likes to use bussmann power blocks in similar situations but these require decent sized enclosures according to the product literature. I’m wondering if there is an easier way?
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Blue wirenuts or Polaris connectors?
What kind of network switch requires a 30 amp 240 volt supply?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
P2PIC_1.jpg
 

vpower1989

Member
Location
USA
Occupation
Engineer
Blue wirenuts or Polaris connectors?
What kind of network switch requires a 30 amp 240 volt supply?

The IT folks apparently use PDUs that run on 208v, 1ph. They can power several switches. The customer has requested the L6-30 receptacles in several locations.
The customer standards typically don’t allow for use of wire nuts for this wire size. They may make an exception in this case.
 

vpower1989

Member
Location
USA
Occupation
Engineer
So it’s looking like there is no way to get around transitioning from the #6 to the smaller wire prior to making the terminations.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
There are two simple choices, run a smaller conductor that will fit on the device or use a blue wire nut and a piece of #10 to terminate to the device. I would question whether or not a receptacle terminal listed for use with a pin adapter.
 

vpower1989

Member
Location
USA
Occupation
Engineer
Haven't seen answer as to why, I too wondering why the need for #6 on a 30 amp?

These particular PDUs require either UPS or Standby power. There are only a a couple UPS and Standby panels in the building. This leads to some very long conductor runs. Trying to maintain a 3% voltage drop from these panels requires the larger conductor size.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
You have to be careful with the pin adapters as to their use at terminations. Many pin adapters have a solid pin, and many terminations are only listed for use with Class B and C stranded conductors. Use of a solid pin adapter on a termination not rated for use with solid conductors is a 110.3(B) violation.
There are pin adapters on the market that have a Class B stranded "pin".
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
These particular PDUs require either UPS or Standby power. There are only a a couple UPS and Standby panels in the building. This leads to some very long conductor runs. Trying to maintain a 3% voltage drop from these panels requires the larger conductor size.
IMO a #10 pigtail to the device is the only viable method unless you move the panel closer to the location of the PDU's.
 