Hey Folks,
I have to connect the power feed from a new lighting contactor to an existing load. The load is far and to prevent excessive voltage drop it is fed with #4 cable. The largest cable accepted in the lighting contactor's terminal block is #10.
In this case I don't have much of a choice because the #4 cable is existing and I have to splice to it. However, if I was doing the whole thing as a new installation I would have done the same thing (#10 from the contactor spliced with a larger conductor to minimize voltage drop). The OCPD is sized for the #10.
Is there anywhere in the NEC that say it is OK to do this? I feel that it is OK; the (smaller) cable is protected, and other than that there is nothing else different from the norm. Would like some confirmation.
Thanks!
I have to connect the power feed from a new lighting contactor to an existing load. The load is far and to prevent excessive voltage drop it is fed with #4 cable. The largest cable accepted in the lighting contactor's terminal block is #10.
In this case I don't have much of a choice because the #4 cable is existing and I have to splice to it. However, if I was doing the whole thing as a new installation I would have done the same thing (#10 from the contactor spliced with a larger conductor to minimize voltage drop). The OCPD is sized for the #10.
Is there anywhere in the NEC that say it is OK to do this? I feel that it is OK; the (smaller) cable is protected, and other than that there is nothing else different from the norm. Would like some confirmation.