First choice for me is to find out if the manafacturer has lugs available that will fit the 500s. Many breakers have diffrent lugs available.
If that is not possible just splice on some conductor that will fit the breaker using a suitable listed connector.
You could try this:
This is the result of either a failure of the person that is doing the take off to pay attention to the size of the cable an number per phase so that the issue can be addressed before and order is entered or the person that is ordering the OCPD without any consideration to what terminal are available. This is where the trouble starts.
They must read the catalog. It is extremely important to make it clear what the cables are that will be terminated even Cu or Al if applicable. The distributor and/or manufacture should address that issue right up front such that the correct or if they aren?t available you certainly will know what trouble you?re in up front instead of getting a surprise.
True sometimes, other times terminations are not available to do the job without changing to different / larger equipment altogether needlessly adding cost to the job.
In Infinity's picture they would have had to buy a greatly oversized transfer switch just to accommodate the conductors chosen to address voltage drop.
I see nothing wrong with the solution shown.
Do you see a problem with the installation in the photo?
One concern i have. The third conductor out of the splice looks smaller than other. I know this part is acting as the breaker lugs which is not needed to be oversized. Do we have limitation for that length?
Well it seems to have 2 large conductors entering the reducer and 1 small conductor going to the OCPD