Hello,
I have a doubt regarding the way of sizing a transformer according to NEC:
¿Why is so oversize?,
Here in Costa Rica we have as law the version 2014 of the NEC, and always is a discution with the utility company the size of the transformers, this due to these companies use a different methodology of calculation, and normally this methodology give a capacity that is less than the half of the NEC calculation or even less.
¿Is the same in USA?
After to do the installation, and check the maximum demand of energy, have you realiced that is really less than the calculated?
I have learnt a way to calculate the size of the transformer using and old formula of the "Rural Electrification Administration” (REA).
DM= FA *FB, where:
FA= N*[1-0.4*N+0.4*root(N²+40)]
FB=0.005925*(E)^(0.885)
Where:
N= Number of consumers
E= kWh average per consumer per month.
To calculate FA and FB, you can use the following formulas:
CF=(FA)/((3.29)(N))
DF=((3.29)(N))/(FA)
Where:
CF= Coincidence Factor
3.29, is a FA value for one consumer.
Example of application:
if there are 406 consumers wich average consume is of 205.9 kWh, is possible to calculate FA and FB according to the formulas, the result wourl be:
FA=414
FB=0.661
DM= 274KW.
My question is:
what metodology of calculation do you use, and why?
Thansks in advace,
I really appreciate any response about this topic.
Regards,
I have a doubt regarding the way of sizing a transformer according to NEC:
¿Why is so oversize?,
Here in Costa Rica we have as law the version 2014 of the NEC, and always is a discution with the utility company the size of the transformers, this due to these companies use a different methodology of calculation, and normally this methodology give a capacity that is less than the half of the NEC calculation or even less.
¿Is the same in USA?
After to do the installation, and check the maximum demand of energy, have you realiced that is really less than the calculated?
I have learnt a way to calculate the size of the transformer using and old formula of the "Rural Electrification Administration” (REA).
DM= FA *FB, where:
FA= N*[1-0.4*N+0.4*root(N²+40)]
FB=0.005925*(E)^(0.885)
Where:
N= Number of consumers
E= kWh average per consumer per month.
To calculate FA and FB, you can use the following formulas:
CF=(FA)/((3.29)(N))
DF=((3.29)(N))/(FA)
Where:
CF= Coincidence Factor
3.29, is a FA value for one consumer.
Example of application:
if there are 406 consumers wich average consume is of 205.9 kWh, is possible to calculate FA and FB according to the formulas, the result wourl be:
FA=414
FB=0.661
DM= 274KW.
My question is:
what metodology of calculation do you use, and why?
Thansks in advace,
I really appreciate any response about this topic.
Regards,