Hi all,
We have an air handling unit that runs (11) supply air fans, each of 11FLA, through a single, internal VFD. The VFD commands the fans to 76Hz. In suspect of this causing each fan to draw more current, possibly totaling higher than the air handling unit breaker is sized for (as found, the VFD does not utilize current-limit setting), we recorded the VFD amperage at this command speed of 76Hz and found that it was only about 110A to run all the fans, which was less than I expected [I guess I expected it to be at least 121A (11 fans x 11 FLA), if not more due to overspeeding the fans past 60Hz.] This isn't particularly my strong suit - can someone help me understand intuitively why this would be the case? As 'fan loads,' shouldn't we expect much higher power required if we're running at 76Hz? ((76/60)^3 times more)?
Also, a more general (but still related) question - is the nameplate maximum overcurrent protection (MOP) of a mechanical unit (such as an air handling unit) calculated under the assumption that the fans won't be run past 60Hz? If, operationally, it is desired to run these fans past 60Hz, do we need to reconsider the sizing of the HVAC unit feeder breaker?
Any guidance would be greatly appreciated.
Thanks much!
Jay
Jay