I saw a previous closed thread on this issue (http://forums.mikeholt.com/showthread.php?t=159284) but it didn't seem like the original question was really cleared up.
When sizing the circuit breaker that will be feeding a packaged/enclosed drive is it sized as you would a normal load 125% of VFD input amps and not specifically a motor controller?
I've always thought that the oversizing of the overcurrent protective device in Table 430.52 was to account for high starting current. A VFD input does not have that significant of a starting current draw and therefore the breaker can be sized for the actual load.
430.122 is very clear on the conductor size being a minimum of 125% of the VFD input amperage. But technically since the VFD OCPD is not discussed and the VFD is by definition a controller Table 430.52 would allow you to way oversize the OCPD for the conductor size?
So, how does everyone size the VFD OCPD? I haven't seen or heard any issues sizing it at 125% of VFD input amps and rounding to next NEMA size up.
Thanks,
rancamEE
When sizing the circuit breaker that will be feeding a packaged/enclosed drive is it sized as you would a normal load 125% of VFD input amps and not specifically a motor controller?
I've always thought that the oversizing of the overcurrent protective device in Table 430.52 was to account for high starting current. A VFD input does not have that significant of a starting current draw and therefore the breaker can be sized for the actual load.
430.122 is very clear on the conductor size being a minimum of 125% of the VFD input amperage. But technically since the VFD OCPD is not discussed and the VFD is by definition a controller Table 430.52 would allow you to way oversize the OCPD for the conductor size?
So, how does everyone size the VFD OCPD? I haven't seen or heard any issues sizing it at 125% of VFD input amps and rounding to next NEMA size up.
Thanks,
rancamEE