Customer owned pad-mounted transformer.2500KVA, 15kV/277-480V. This transformer is deadfront construction with loadbreak elbows at the front. No live part present in the transformer. Does the table 110.34(A) still apply?
110.34(A) reads:
? Equipment likely to require examination, adjustment, servicing, or maintenance while energized shall clear working space in the direction of access to live parts the electrical equipment and shall not be less than specified in Table 110.34(A).?
Typically, we?ve been provided 5 ft around a transformer for maintenance purpose not to meet this requirement. But this has been brought up during the code review.