Pad Mounted Transformers

Status
Not open for further replies.

charlie

Senior Member
Location
Indianapolis
Re: Pad Mounted Transformers

Sure, as long as it is completely enclosed, vented to the outside, and meets the construction specifications of a transformer vault. A PMT is normally filled with mineral oil and is very flammable if it ruptures. The basic answer is no but provisions can be made to install a mineral oil transformer just about anywhere, see Article 450, Part III (starts with Section 450.41). :D
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: Pad Mounted Transformers

The phrase ?transformer vault? carries very specific construction requirements, but it is seldom invoked by the code. An indoor transformer that is oil filled requires a vault. An indoor transformer that is dry-type does not require a vault, unless it is rated above 35,000 volts. But you would have seen this, when you read the section that the Other Charlie cited.
 