Re: Paddle Fan and Smoke Alarm
We occasionaly have the case where the room has multiple obstacles for the smoke alarm placement. Between staying within 36" of the highest point, 36" from the supply register, 36" from a bathroom door, and now 36" from the ceiling fan, it can be a little difficult.
In these situations, I feel a compromise is needed. Through conversations with a State Fire Marshall, encroaching in on the space away from the suppy register can be relaxed if not in the direct air flow. Also, the design of the bathroom may permit the smoke alarm closer to the room's door without being a nuisance. So really, it just comes down to finding the best fit when the smoke alarm will be most effective.