Does a padlock attachment on a din rail mounted CB constitute an acceptable disconnecting means for a group of small single phase motors fed from that CB?
petersonra said:Does a padlock attachment on a din rail mounted CB constitute an acceptable disconnecting means for a group of small single phase motors fed from that CB?
jim dungar said:Why do you ask? Do you think this would be any different than if the breaker was mounted into a panelboard?
Providing that:Does a padlock attachment on a din rail mounted CB constitute an acceptable disconnecting means for a group of small single phase motors fed from that CB?
davidr43229 said:Providing that:
3. The person taging is out is "qualified person with Arc Flash PPE".
don_resqcapt19 said:Bob,
Who would be expected to use the disconnect? I would expect that you would have to open the panel and be exposed to energized parts to operate and apply the lock to the disconnect. That would require an electrically qualified person.
Don
jim dungar said:The person should also have voltage rated PPE. And provide appropriate placed barricades while the enclosure door is open.
Everyone please remember Electrical Safe Work Programs (NFPA 70E) involve a whole lot more than just arc flash protection.
davidr43229 said:Providing that:
1. is a UL489 rated breaker with a HP rating, Not a UL1077 Suplementary Breaker.
2. Is within sight of the motor
3. The person taging is out is "qualified person with Arc Flash PPE"
There are many reasons why you may want to shut off those small motors and keep the main panel running.
Once all the above is met then.....Yes Panduit & other manufacturers make a lock out, for them.
I don't know what your application is, but in many cases the maching operator needs to be able to lock the equipment out to clear jams or other minor service work. This person would not normally be qualified to open the equipment and operate the disconnect.The end user is responsible for determining who is qualifed to use the disconnect.
petersonra said:Arc flash protection on a 20A 120V circuit?
mdshunk said:How about a lock on the JIC enclosure that's housing that DIN rail breaker?
don_resqcapt19 said:Bob,
I don't know what your application is, but in many cases the maching operator needs to be able to lock the equipment out to clear jams or other minor service work. This person would not normally be qualified to open the equipment and operate the disconnect.
Don
The origional thread here was can you use a CB as a disconnect, within the panel. The answer is yes and the "lock out" has to fit that CB.Does it have to be on the breaker itself
Most companies that recognize the NFPA-70E are disallowing operators to preform this task, due to them not being qualified, certified or trained and have posted memo's to this effect. Tis a cultural change.I don't know what your application is, but in many cases the maching operator needs to be able to lock the equipment out to clear jams or other minor service work. This person would not normally be qualified to open the equipment and operate the disconnect.
davidr43229 said:Don,
Most companies that recognize the NFPA-70E are disallowing operators to preform this task, due to them not being qualified, certified or trained and have posted memo's to this effect. Tis a cultural change.
Just my $.02
Define routine chores please?perform routine operator chores on it