padlock attachment on cb

Status
Not open for further replies.

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Does a padlock attachment on a din rail mounted CB constitute an acceptable disconnecting means for a group of small single phase motors fed from that CB?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
petersonra said:
Does a padlock attachment on a din rail mounted CB constitute an acceptable disconnecting means for a group of small single phase motors fed from that CB?

Why do you ask? Do you think this would be any different than if the breaker was mounted into a panelboard?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Bob,
Who would be expected to use the disconnect? I would expect that you would have to open the panel and be exposed to energized parts to operate and apply the lock to the disconnect. That would require an electrically qualified person.
Don
 

davidr43229

Senior Member
Location
Columbus, Oh
Does a padlock attachment on a din rail mounted CB constitute an acceptable disconnecting means for a group of small single phase motors fed from that CB?
Providing that:
1. is a UL489 rated breaker with a HP rating, Not a UL1077 Suplementary Breaker.
2. Is within sight of the motor
3. The person taging is out is "qualified person with Arc Flash PPE"

There are many reasons why you may want to shut off those small motors and keep the main panel running.
Once all the above is met then.....Yes Panduit & other manufacturers make a lock out, for them.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
davidr43229 said:
Providing that:
3. The person taging is out is "qualified person with Arc Flash PPE".

The person should also have voltage rated PPE. And provide appropriate placed barricades while the enclosure door is open.

Everyone please remember Electrical Safe Work Programs (NFPA 70E) involve a whole lot more than just arc flash protection.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
don_resqcapt19 said:
Bob,
Who would be expected to use the disconnect? I would expect that you would have to open the panel and be exposed to energized parts to operate and apply the lock to the disconnect. That would require an electrically qualified person.
Don

The end user is responsible for determining who is qualifed to use the disconnect.

That is a good point though.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
jim dungar said:
The person should also have voltage rated PPE. And provide appropriate placed barricades while the enclosure door is open.

Everyone please remember Electrical Safe Work Programs (NFPA 70E) involve a whole lot more than just arc flash protection.

Arc flash protection on a 20A 120V circuit?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
davidr43229 said:
Providing that:
1. is a UL489 rated breaker with a HP rating, Not a UL1077 Suplementary Breaker.
2. Is within sight of the motor
3. The person taging is out is "qualified person with Arc Flash PPE"

There are many reasons why you may want to shut off those small motors and keep the main panel running.
Once all the above is met then.....Yes Panduit & other manufacturers make a lock out, for them.

1. Is a Square D QOU breaker.
2. Within 5 feet or so.
3. Not up to me.

Keeping the panel live while locking out one or more motors is not a design criteria in this case.
 

davidr43229

Senior Member
Location
Columbus, Oh
Bob,
Yes
Anything over 50 volts. My "guess" would be voltage rated 00 gloves, untreated clothing of 4.5 oz and safety goggles with sideshields (level 0) and a barrier of 4-5" but usually most people use a standard default of 4', unless a Engineering Arc Flash calculation has been done.
Just my $.02
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Bob,
The end user is responsible for determining who is qualifed to use the disconnect.
I don't know what your application is, but in many cases the maching operator needs to be able to lock the equipment out to clear jams or other minor service work. This person would not normally be qualified to open the equipment and operate the disconnect.
Don
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
petersonra said:
Arc flash protection on a 20A 120V circuit?

I mentioned voltage PPE. NFPA70E is about all aspects of electrical safety, not just arc flash.

A qualified individual is one that is trained to perform that specific task. It is totally possible for a machine operator to be trained to open and perform a LOTO operation in a control panel but not be qualified for any other electrical task. Likewise, it is possible to be trained to make electrical terminations on de-energized equipment but not be qualified to perform a LOTO operation.
 

realolman

Senior Member
mdshunk said:
How about a lock on the JIC enclosure that's housing that DIN rail breaker?

That is something I have wondered about, before... a breaker inside an enclosure with a lock on the enclosure. Seems good to me, but I wonder if it is. Does it have to be on the breaker itself?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
don_resqcapt19 said:
Bob,

I don't know what your application is, but in many cases the maching operator needs to be able to lock the equipment out to clear jams or other minor service work. This person would not normally be qualified to open the equipment and operate the disconnect.
Don

Not an issue on this piece of equipment, but a good point.
 

davidr43229

Senior Member
Location
Columbus, Oh
Don,
Does it have to be on the breaker itself
The origional thread here was can you use a CB as a disconnect, within the panel. The answer is yes and the "lock out" has to fit that CB.
I don't know what your application is, but in many cases the maching operator needs to be able to lock the equipment out to clear jams or other minor service work. This person would not normally be qualified to open the equipment and operate the disconnect.
Most companies that recognize the NFPA-70E are disallowing operators to preform this task, due to them not being qualified, certified or trained and have posted memo's to this effect. Tis a cultural change.
Just my $.02
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
davidr43229 said:
Don,
Most companies that recognize the NFPA-70E are disallowing operators to preform this task, due to them not being qualified, certified or trained and have posted memo's to this effect. Tis a cultural change.
Just my $.02

Are you suggesting that companies are requiring that an electrician come lockout a machine to perform routine operator chores on it?
 