I know less about the construction of Classified areas than I do the electrical systems therein but I have set of prints for a paint mix room that calls for the area to be Class1 Div 1. The construction is sheetrock on metal studs. Doesn't seem to right for a C1D1 area. Input appreciated !
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I know less about the construction of Classified areas than I do the electrical systems therein but I have set of prints for a paint mix room that calls for the area to be Class1 Div 1. The construction is sheetrock on metal studs. Doesn't seem to right for a C1D1 area. Input appreciated !

maybe they are blowout walls.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
new term... If so, how would that affect his wiring method ?
It doesn't; Section 501.10(A) still applies. I've had a few "blowout" ceilings/roofs before but walls would be a bit dangerous. In any case the room construction itself it determined by the Uniform Building Code or whatever the local building code is. The room's physical construction only needs to be able to provide the various 3xx.30 Securing and Supporting requirements of the relevant wiring method.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
I know less about the construction of Classified areas than I do the electrical systems therein but I have set of prints for a paint mix room that calls for the area to be Class1 Div 1. The construction is sheetrock on metal studs. Doesn't seem to right for a C1D1 area. Input appreciated !

That seems a little lightweight to support the fixtures, raceway, and fittings that are required. Is it double-rocked with 1/2 or 5/8 board?
 