Thank you! The actual issue I'm facing, there is one paintbooth fixture recessed in wall that is close to paintbooth door (within 3-ft). My understanding anything within 3 ft (all direction) of any paintbooth opening needs to be Class I, Div 2. So, I'm not sure if this installation meet that NEC requirement. Any thoughts? ThanksSurface mounted is a common option and usually acceptable; however, there are alternatives. See Section 516.6(C).
It could be helpful to your cause if you specified the cut sheet to the fixture your using, and whether the booth wall is a bare or insulated panel. Depending, fixtures can be mounted exterior to the panels or inside the panels, their listing classification is a determining factor on how they can be wired.Thank you! The actual issue I'm facing, there is one paintbooth fixture recessed in wall that is close to paintbooth door (within 3-ft). My understanding anything within 3 ft (all direction) of any paintbooth opening needs to be Class I, Div 2. So, I'm not sure if this installation meet that NEC requirement. Any thoughts? Thanks
Inside the spray booth is CI, D1 per the solid hatching. If you look at the elevation you can see the top of the hatch (CI, D2) stops at the top and doesn't extend down to inside the booth or even interior walls or ceilings.I think the top and bottom openings are sealed devices located on the back side of the wall, while the side ones are maybe doors of some sort? Although why the inside of the spray booth adjacent to the door would only be div 2 and the rest of the interior of the spray booth is div 1. So that is probably not it.
these fixtures are installed outside of the spray area.It could be helpful to your cause if you specified the cut sheet to the fixture your using, and whether the booth wall is a bare or insulated panel. Depending, fixtures can be mounted exterior to the panels or inside the panels, their listing classification is a determining factor on how they can be wired.
Paint / Powder / Blast Booth
MTW, thanks for your input. Here is a photo of what I'm referring to. As you, these openings, which is with 3ft of the door, are for light fixtures (not rated for hazardous locations) and has a glass panel that separate it from paintbooth interior. The wiring goes inside the walls or whatever you want to call them.Back the within the walls??? There is an inside or an outside, what is within? The only way to have a within the wall is with an insulated panel. In wiring booths for more than 30 years I only ever encountered one booth style that had indulated panels with the fixture in the walls and they had molded glass covers to enclose the fixtures and haven't made that type in many years. I think your reading into the illistration more than need be. It's a single barrier wall, can't have a within with only one layer construction, even though the illustration may look like it.