Same here, maybe just a CMP oversight.
I submitted a PI for 2023 to expand Exception 1 to cover any application, with the substantiation:
"The current language is unnecessarily restrictive as to the applications that are permitted for parallel
conductors smaller than 1/0 AWG. When the conditions specified in the exception are met, there is no
safety downside to using parallel conductors in smaller sizes. Thus in keeping with the goal of
"Practical Safeguarding" as specified in 90.1(A), there is no reason to restrict paralleling conductors in
small sizes when each conductor is protected at its individual ampacity."
The CMP response:
"Resolution: No substantiation for opening up this exception further. Currently allowed applications are
low current."
I guess if you disagree you will soon have a short window of time to provide a Public Comment on my Public Input 3480-NFPA 70-2020 (if I've got the lingo correct).
Cheers, Wayne