Panel above trough
quogueelectric
new york
I think I remember that a panel above a trough had to be brought out to the same distance off the wall as the trough but I cant find the code section???
You won't find that rule. This is the only rule I know of that applies:
110.26(C) Height of Working Space. The work space shall be clear and extend from the grade, floor, or platform to the height required by 110.26(E). Within the height requirements of this section, other equipment that is associated with the electrical installation and is located above or below the electrical equipment shall be permitted to extend not more than 152 mm (6 in.) beyond the front of the electrical equipment.
Thank you I had just found it and was calling off the experts. Thanks again.