Panel Access

Status
Not open for further replies.

MichaelJ

Member
Location
Georgia
Any problem with main electrical service (breaker panel) Located in a 2nd floor mech room with only acess from a pull down stair way.
 
Are you talking about the service disconnecting means or just a panelboard fed from the service disconnecting means?

Chris
 
Overcurrent devices are required to be readily accessible. If you have a permanent pull down ladder and don't have to resort to getting a portable ladder to access the panel and it's overcurrent devices it would be readily accessible.

Does this panel have the required working space clearances of 110.26(A)?

Also I mentioned the service disconnecting means. The reson that I asked that is that the service disconnecting means must be installed either outside the building or inside nearest the point of entrance to the building. (See 230.70(A)(1))

Chris
 
Any problem with main electrical service (breaker panel) Located in a 2nd floor mech room with only acess from a pull down stair way.

I assume "access" means access to the room, and
not "access" to the breakers, which would be 240.24(F).

I would not interpret it this way, but I suppose
there could be an interpretation of a pull-down
stairway as "so forth" wrt 240.24(A) req't for "readily
accessible) in article 100 " ... without requiring... to
resort to portable ladders, and so forth."
 
Overcurrent devices are required to be readily accessible. If you have a permanent pull down ladder and don't have to resort to getting a portable ladder to access the panel and it's overcurrent devices it would be readily accessible.

I didn't see this before my previous post. I think this
makes total sense and is more clearly stated than
what I said.
 