Here is a question for all who would like to respond.
The enclosure for a panel board has a 3" conduit entering the bottom without a suplimental equipment ground installed. The ground terminal bar is located on the panelboard which is adjusted out from the back of the enclosure to flush up with the cover. The conduit is being use as an equipment ground. Would the enclosure infact be used here as a equipment bonding jumper???
Is the enclosure listed and or labled for this application and for the sake of argument we could use lets say a GE enclosure or any enclosure for that matter????
The panel board instruction say to bond the equipment terminal bar to the enclosure and to terminate all equipment grounds to the terminal bar provided.
The enclosure for a panel board has a 3" conduit entering the bottom without a suplimental equipment ground installed. The ground terminal bar is located on the panelboard which is adjusted out from the back of the enclosure to flush up with the cover. The conduit is being use as an equipment ground. Would the enclosure infact be used here as a equipment bonding jumper???