There is no NEC requirement that a panelboard must be limited to 80% of it's capacity.
Branch circuits and feeders must be sized at 125% of the continious load plus 100% of the non-continious loads, this might be what you are thinking.
Take a look at 210.19(A)(1) and 215.2(A)(1).
Chris