This is actually a two-part query so if I need to split it up please let me know. We have a number of traffic related panels (3R roadside like you see at an intersection) that powers message signs, cameras, detectors etc. that are going in place of existing cabinets that had a panel board for power distribution mounted to the side of the cabinet. The Incoming feed is 240V single phase going to a combination of 120V and 240V equipment and there are no motor controls. To provide a cleaner installation a new panel board was provided and mounted inside the enclosure. It's a standard panel board with a main breaker and some branch breakers. A local electrician is now stating that 1) the panel board has to have three feet of clearance within the enclosure by NEC 110 and 2) there has to be a lockable disconnect within 50 feet of the enclosure. Everyone seems split 50/50 concerning the panel board and I haven't seen anything specific about their use inside an enclosure. In 35 years of panel design I don't know that I have ever had to provide an external disconnect for a panel with non-motor loads and these panels are often fed from a main panel board that could be a half mile away. I pinged our local UL inspector but haven't heard anything from him for two weeks. Any enlightenment you might provide would be greatly appreciated.