Panel boards in restrooms?

Status
Not open for further replies.

earlydean

Senior Member
Re: Panel boards in restrooms?

240.24(E)In dwelling units and guest rooms of hotels and motels, overcurrent devices, other than supplementary OC protection, shall not be located in bathrooms. Any other occupancy is's OK.
Panelboards usually contain OC devices. QED
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Panel boards in restrooms?

Also 230.70(A)(2) says that the service disconnet cannot be in a bathroom. This section applies to all occupancies.
Don
 

gwz2

Senior Member
Location
Indiana
Re: Panel boards in restrooms?

Don,

What is the rule when a person must traverse a bath room to get the the Service Equipment room ? ( commercial site )

gwz2
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: Panel boards in restrooms?

The rule is that you must wash your hands before entering the electric room. :roll:
 
G

Guest

Guest
Re: Panel boards in restrooms?

What year was 230.70(A)(2) enacted? I need to go way back here :)
 