panel bonding from transformer
Section 250.30(A)(1) is very clear as to where the grounded (neutral) conductor on a SDS is to bonded, it states the following;
(1) System Bonding Jumper. An unspliced system bonding jumper in compliance with 250.28(A) through (D) that is sized based on the derived phase conductors shall be used to connect the equipment grounding conductors of the separately derived system to the grounded conductor. This connection shall be made at any single point on the separately derived system from the source to the first system disconnecting means or overcurrent device, or it shall be made at the source of a separately derived system that has no disconnecting means or overcurrent devices.
We installed 3 phase 4 wire with an egc to panel to main cb in panel.
The conductor you noted as egc, should be noted as a equipment bonding jumper (EBJ) which is required to be sized per 250.30(A)(2).
Inspector gave us a violation based on article 250.92 for neutral not bonded.
When quoting code rulers you don?t state article 250.92 the proper quote would be section 250.94 or just 250.94.