I?ve got one for you. It?s residential. You have a 400amp service rated meter can on the side of a house. There are (2) separate feeders going to (2) separate 200amp panels that are side by side inside the house. Both panels are the first means of disconnect. One of the panels has the ground wire coming from the rebar. The other panel has the bond wire going to the cold water copper pipe. Now here?s the question: Should there be a common bond wire between the (2) panels? My answer is no. By doing so you would be paralleling you neutral and causing a loop in your grounded system. The panels are already bonded together at the service entrance, the meter can neutral lugs. Why bond them together again with an addition jumper between the panels? Some inspectors in my area are requiring the additional jumper. Should they? If so, why?