shawn73
Member
- Location
- Napoleon, Ohio
I am an Industrial Electronic Technician in our automotive factory. The 6 of us (2 per shift) are responsible for all of the electrical work, plc programming, and machine electrical troubleshooting in our facility. I have been trying to find a good answer to this question with confident back-up information for some time. I would really appreciate some input.
We are responsible for our electrical system once it enters our facility, usually throuh 3-4,000 amp 480V, 3 phase panel. Typically from that point we run 400-800 amp, 480V, 3 phase to another panel for distribution smaller distribution such as to a 480V Delta, 208/120 Wye transformer providing 200 amps for typical recepticals, etc. This is where I start to have questions.
Lets say I just finished wiring the 200 amp 208/120V panel described above. I now need to install a 60 amp subpanel fed from the 200 amp panel. Should both the 200 amp and 60 amp 208/120V panels have bonded neutrals?? I have always had a difficult time with is issue because bonding a ground to a neutral creates a parallel neutral wire. I have been told by some people that your neutral should not carry any current, but I'm not confident of this because of all I have read about harmonics currents.
Another example:
We recently had an outside contractor add a 60 amp 208/120V service to a small building outside our main facility (No foundation, just a sitting 12X14 metal building). I was required to run conduit etc, in the building and found that the 60 amp panel was not bonded and there was not a ground rod driven for the equipment ground. (So, the metal building could have been electrified.) I understand that there should not be another ground rod driven because of potential between ground rods, but if I bond the neutral to ground in the 60 AMP panel I again create a parallel neutral.
These are both examples of issues I encounter from day to day. I want to do things correctly, but I cannot seem to get a confident answer form anyone I ask. Thank you all for your help.
We are responsible for our electrical system once it enters our facility, usually throuh 3-4,000 amp 480V, 3 phase panel. Typically from that point we run 400-800 amp, 480V, 3 phase to another panel for distribution smaller distribution such as to a 480V Delta, 208/120 Wye transformer providing 200 amps for typical recepticals, etc. This is where I start to have questions.
Lets say I just finished wiring the 200 amp 208/120V panel described above. I now need to install a 60 amp subpanel fed from the 200 amp panel. Should both the 200 amp and 60 amp 208/120V panels have bonded neutrals?? I have always had a difficult time with is issue because bonding a ground to a neutral creates a parallel neutral wire. I have been told by some people that your neutral should not carry any current, but I'm not confident of this because of all I have read about harmonics currents.
Another example:
We recently had an outside contractor add a 60 amp 208/120V service to a small building outside our main facility (No foundation, just a sitting 12X14 metal building). I was required to run conduit etc, in the building and found that the 60 amp panel was not bonded and there was not a ground rod driven for the equipment ground. (So, the metal building could have been electrified.) I understand that there should not be another ground rod driven because of potential between ground rods, but if I bond the neutral to ground in the 60 AMP panel I again create a parallel neutral.
These are both examples of issues I encounter from day to day. I want to do things correctly, but I cannot seem to get a confident answer form anyone I ask. Thank you all for your help.