How many of you series two 240 volt control relay coils to make use of the 480 being supplied to the unit?
Customer supplied roto phase.
Customer supplied roto phase.
It is what they did.I wouldn't trust the coils to be similar enough to divide the voltage equally.
I don't see them being that much different that they won't still be within a reasonable tolerance. HVAC guys parallel control transformers when "twinning" units sometimes, I think there is more risk of unequal division issues with something like that.I wouldn't trust the coils to be similar enough to divide the voltage equally.
Kind of is a hack, and shouldn't be original design, but does work in a pinch when servicing, usually with intent to come back and replace with the right item.If they’re identical relays, it probably works fine. Still seems like a hack.
Brand new out of the box yesterday.Kind of is a hack, and shouldn't be original design, but does work in a pinch when servicing, usually with intent to come back and replace with the right item.
Or a single relay with more poles.The other way is to parallel the two coils, if two relays are really needed, and use a step-down transformer for power.
If you are talking about a UL508a inspector, I suspect they would not even notice unless it was their quarterly point of emphasis item.A UL inspector would not likely allow it, you are using the relays in a way not intended per their listing.
If they are in series, current is always going to be the same through both coils. Voltage drop across each individual coil can vary if impedances are not the same though.In this scenario what stops the current from choosing one relay over the other? I see a potential imbalance of load on one of the relays. In the case of this imbalance you might burn out one of the relays... This issue comes about because of the possible difference in coil resistance...this can not be guaranteed to match perfectly from relay to relay even of the same p#. Just my 2 cents, Thanks!