400A panel, 480V, 3phase (no neutral), fed from 480/277V system but neutral not brought to panel.
The panel feeds 480V, single phase infrared heaters. This is an old building, they used 3-pole breakers to feed groups of heaters, it turns out that each breaker has unbalanced phase currents (they alternate the phase connections for each heater, AB, BC, CA). There is no neutral branch circuit conductors. I am thinking that this may have caused the bus bar to over heat. The individual heaters do not need neutral, but combining multiple heaters on 3-pole breakers create unbalanced currents. The main breaker did not trip so this is probably not an overload situation. I am waiting for name plate data of the heaters to run a load calc on the panel. Do you think the unbalanced branch circuit currents can cause the panel bus bar to overheat?
The panel feeds 480V, single phase infrared heaters. This is an old building, they used 3-pole breakers to feed groups of heaters, it turns out that each breaker has unbalanced phase currents (they alternate the phase connections for each heater, AB, BC, CA). There is no neutral branch circuit conductors. I am thinking that this may have caused the bus bar to over heat. The individual heaters do not need neutral, but combining multiple heaters on 3-pole breakers create unbalanced currents. The main breaker did not trip so this is probably not an overload situation. I am waiting for name plate data of the heaters to run a load calc on the panel. Do you think the unbalanced branch circuit currents can cause the panel bus bar to overheat?