Good morning, I am an electrician at a WWTP. I have a 200A panel that is full, and it has been requested to add a 480V 45kw 54A water heater.
There is a power monitor unit (20A) that we plan to remove in order to make room for the water heater breaker. However reviewing the power meter, I see it keeps the highest KW value, this was 69.9kw. Using 220.87 I think found I found that adding the 45kw unit will be over loading the rated service.
Max load at 125% plus new load must not exceed the rating of the service (200A).
I would like confirmation on my calculations.
W/V+25%+new load Amps= full load amps
69900W/467=149.67 x 25% = 37.42
149.67A + 37.42= 187.09A
187.09A + 54A = 241.09A
41A over 200A rated main.
Thanks for all input.