See attached photo. I have an issue with a comment the plans examiner is making.
This was the original comment: "Clearance from panel H1 to edge of door on E100 is insufficient. Please revise to show the door clearance requirements are met for one exit. See section 110.26 for clearance requirements in the 2008 NEC."
Now I assumed since panel H1 was a 1200A panel that he was talking about 110.26(C)(2) even thought the panel isn't over 6 feet wide. That would require me to have a second means of egress from the space if it were 1200A and 6 feet wide. So I thought he was commenting on exception (b) in that section (although it wouldn't apply here).
This was the response back to the reviewer from our project manager: "We are in receipt of your plan review comments dated 5/31/16. I’ve discussed your comment about the clearances with my electrical engineer and he believes he is showing proper clearances. Panel H1 is located on the east wall of the room. The door is located in the northwest corner of the room and swings out. More than double the required clearance has been provided in front of panel H1 {even though panel H1 is not 6 feet wide per 110.26(C)(2)} allowing for a single exit from the room."
So now he just replied with this: "Unfortunately, on page E100, it shows a 500 amp panel labeled L1 to be less than 3' from edge to single egress point. The exception in the 2008 NEC being quoted for the utilization of a single egress from this space also prohibits the location of panels and equipment within the clear distances of table 110.26(A)(1)."
So now I'm completely confused as to what he's referring to. He has now changed his comment from panel H1 to panel L1 and panel L1 is only 500A. I called him for clarification, but as per usual no one answered. Does anyone have any idea what this reviewer could be referencing? I am unaware of any rule that would not allow panel L1 to be located where it is.
Thanks,
-Drew
This was the original comment: "Clearance from panel H1 to edge of door on E100 is insufficient. Please revise to show the door clearance requirements are met for one exit. See section 110.26 for clearance requirements in the 2008 NEC."
Now I assumed since panel H1 was a 1200A panel that he was talking about 110.26(C)(2) even thought the panel isn't over 6 feet wide. That would require me to have a second means of egress from the space if it were 1200A and 6 feet wide. So I thought he was commenting on exception (b) in that section (although it wouldn't apply here).
This was the response back to the reviewer from our project manager: "We are in receipt of your plan review comments dated 5/31/16. I’ve discussed your comment about the clearances with my electrical engineer and he believes he is showing proper clearances. Panel H1 is located on the east wall of the room. The door is located in the northwest corner of the room and swings out. More than double the required clearance has been provided in front of panel H1 {even though panel H1 is not 6 feet wide per 110.26(C)(2)} allowing for a single exit from the room."
So now he just replied with this: "Unfortunately, on page E100, it shows a 500 amp panel labeled L1 to be less than 3' from edge to single egress point. The exception in the 2008 NEC being quoted for the utilization of a single egress from this space also prohibits the location of panels and equipment within the clear distances of table 110.26(A)(1)."
So now I'm completely confused as to what he's referring to. He has now changed his comment from panel H1 to panel L1 and panel L1 is only 500A. I called him for clarification, but as per usual no one answered. Does anyone have any idea what this reviewer could be referencing? I am unaware of any rule that would not allow panel L1 to be located where it is.
Thanks,
-Drew