I am installing a 200 amp service on a post being feed underground. The utility company allows the meter to be a minimum of 3 ft. above ground and I cannot seem to find a minimum circuit breaker distance above ground in the NEC.
(except for trailer parks and places where inspectors enforce a "snow height")
And what snow height requirement would that be?
Chris
and there is always the problem of the breakers (assuming there are breakers in the panel)
240.24 Location in or on Premises.
(A) Accessibility. Overcurrent devices shall be readily accessible and shall be installed so that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 2.0 m (6 ft 7 in.) above the floor or working platform, unless one of the following applies: