Can someone tell me what NEC Article prohibits a panel enclosure being used as a raceway?
thanx in advance.
Not a one, it is allowed.
See 312.8 and make sre to read through all of it.
This is a common install, it's darn hard to overfill a panel.thanks iwire,
One of my electricians decided to feed Panel B through Panel A (installed next to each other). Since this feeder to panel B serves an overcurrent device (MCB), 312.8 prohibits this unless the enclosure fill is 40% or less.
Is this your interpetation as well?
thanks iwire,
One of my electricians decided to feed Panel B through Panel A (installed next to each other). Since this feeder to panel B serves an overcurrent device (MCB), 312.8 prohibits this unless the enclosure fill is 40% or less.
Is this your interpetation as well?
Exactly. If the wireway is 3"x3" (and in many panels it is larger) a 40% fill would be four 500kcmil plus 57 #12s (assuming THHN).Yes however there is no way it is approaching 40% fill.