EEDude
Member
- Location
- Spfld Area, MA
Hi Everyone,
I am looking at a 100A MLO panel (ELP1 in the attached image) protected upstream by a 100A breaker and fed by #1AWG. There is a feed through utilizing the feedthrough lugs in this panel. The feedthrough conductors are also #1AWG (200ft) and land in another downstream 100A MLO panel (ELP5 in the attached image).
I have attached a fundamental oneline which reflects the system. I have also attached an image I found in an earlier post that had a similar configuration (but a different question) which gives a little better graphic of what it would look like.
408.36 should be covered.
So, the burning question is, are the conductors leaving the original panel considered a tap? They are the same size, so I'm saying no. At this point, I can find nothing that would prohibit the configuration in the attached regardless of the length of feedthrough conductor.
Appreciate the input...
I am looking at a 100A MLO panel (ELP1 in the attached image) protected upstream by a 100A breaker and fed by #1AWG. There is a feed through utilizing the feedthrough lugs in this panel. The feedthrough conductors are also #1AWG (200ft) and land in another downstream 100A MLO panel (ELP5 in the attached image).
I have attached a fundamental oneline which reflects the system. I have also attached an image I found in an earlier post that had a similar configuration (but a different question) which gives a little better graphic of what it would look like.
408.36 should be covered.
So, the burning question is, are the conductors leaving the original panel considered a tap? They are the same size, so I'm saying no. At this point, I can find nothing that would prohibit the configuration in the attached regardless of the length of feedthrough conductor.
Appreciate the input...