400 amp bus and 400 amp main so a 400 amp feeder is likely what they want. What it doesn't show is how it connected in the existing PP-EQ-1 panel. Since they're next to each other and there is a main CB a tap could work. A 400 amp tap would require 600 kcmil conductors if there is a 400 amp OCPD in PP-EQ-1 then 500 kcmil would be sufficient.here? I guess if I just use a 400A feeder I'd be safe?
No schedule for PP.Sure.
The new panel show 0 va.
Does show a new unit with an 80 amp breaker.
Nothing against feeding the panel with a smaller feeder as long as it carries the load.
Personally I would RFI the feeder.
Hopefully you can get a 400 in that 600 with out changing it out. Any idea what panel PP is. That's a starting point.
Edit:
I see the new has a 400 amp main. If the 600 has feed thru lugs you may be able to do a tap. Be sure to size the tap conductors for 400 amps.