Is using a panel lock out that prevents the main breaker from being turned on when back feeding the panel with a 30amp inlet and breaker from a generator legal.
I see lockouts that are listed and not listed with a particular panel cover. If it's listed, can you use these lockouts to backfeed a 200 amp panel with a 30 amp generator? Or will it not be legal because the generator isn't sized for a 200 amp load even though it's on a 30 amp breaker? If it's legal great, if not would the only way wire a portable generator be by using one of those those sub panel transfer switches with 8 or 12 circuits and amp meters?
Thank you
I see lockouts that are listed and not listed with a particular panel cover. If it's listed, can you use these lockouts to backfeed a 200 amp panel with a 30 amp generator? Or will it not be legal because the generator isn't sized for a 200 amp load even though it's on a 30 amp breaker? If it's legal great, if not would the only way wire a portable generator be by using one of those those sub panel transfer switches with 8 or 12 circuits and amp meters?