Panel identification

Status
Not open for further replies.
Good point. In any event the breaker must be marked as being the main to your point.

I haven't looked it up in the NEC, but I know that one of the AHJ here requires panels to be marked "not the only service" or "mulitple services" if there is more than one panel in a commercial/industrial environment. Something similar to the requirements when Solar is used along with the grid.
 
NEC 408.4 said:
Field Identification Required.
(A) ...
(B) Source of Supply. All switchboards and panelboards supplied by a feeder in other than one- or two-family dwellings shall be marked to indicate the device or equipment where the power supply originates.
 