Panel in high rise residential unit

Status
Not open for further replies.

sharan

Senior Member
Can we put electrical panelboard in the clothes closet (residential unit), but behind the door where there are no clothes hangers?
 
The panel can be installed in the bathroom but, you can't put any breakers in it.

240.24(E)

(E) Not Located in Bathrooms In dwelling units and guest rooms or guest suites of hotels and motels, overcurrent devices, other than supplementary overcurrent protection, shall not be located in bathrooms.

Roger
 
As long as you maintain the needed clearance of 110.26(A). You actually have a closet where the door opens into the closet?
 
sharan said:
Can we put electrical panelboard in the clothes closet (residential unit), but behind the door where there are no clothes hangers?

NO. There is no difference between a clothes closet in a single family home or a high rise multi family apt.
 
Panel in clothes closet

Panel in clothes closet

sharan said:
Can we put electrical panelboard in the clothes closet (residential unit), but behind the door where there are no clothes hangers?

My question is clothes closet, not bathrooms.
 
Boy, I must have really been sidetracked. Anyways, it is as Acrwc10 points out.

Roger
 
Ok, got caught up, my first post should have been.


The panel can be installed in the clothes closet but, you can't put any breakers in it.


240.24(D)

(D) Not in Vicinity of Easily Ignitible Material Overcurrent devices shall not be located in the vicinity of easily ignitible material, such as in clothes closets.


Roger
 
LarryFine said:
You really must have needed to go when you typed that. :roll:

LOL, actually, it was a couple of phone calls.

Roger
 